Please helpšŸ™Upgraded to 1.5kw 220v spindle and having disconnect issues 😭

I was hoping for resistance measurements at the VFD terminals with the spindle connected (and circuit breaker off for safety).
PD141 = 220 spindle rated voltage?
PD142 = 7 spindle rated current?
PD143 = 2 pole motor?
PD144 = 3600?

R-S Should be ~ 240 Vac
R-E Should be ~120 Vac
S-E Should be ~120 Vac